Can 208V loads and 120V loads be in the same panel? If so how are they wired in the panel.

Assuming the panel has a neutral included with the feeder yes absoulutly.

They get wired like they do in any panel, white conductor to the neutral bar and the hots to the breakers.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Assuming the panel has a neutral included with the feeder yes absoulutly.

They get wired like they do in any panel, white conductor to the neutral bar and the hots to the breakers.

Any line-to-line loads need to be fed by a multi-pole breaker that opens both/all ungrounded line conductors simultaneously. An MWBC with only line-neutral loads can use single pole breakers with handle ties instead.

Although there is no prohibition against it in the code AFAIK, I would try to avoid running both line-line loads and unrelated line-neutral loads off the same branch breaker, especially in a three phase system.
 