OCPD for branch circuit

Status
Not open for further replies.

Adnan Hasan

Member
Location
baghdad, Iraq
the contractor use one OCPD for branch circuit supplying 5 Fan Coil Units (FCU). each FCU install in separate apartment (total 5 apartments). OCPD installed in one of those 5 apartment. power of FCU is 800 w at 230 v 50 Hz.
Q1: considering each separate apartment as single dwell, OCPD shall be installed together with FCU in same apartment. right? please refer to code.
Q2: is it permitted to connect 5 FCU on the same branch with one OCPD?
thanks in advance.
 

Adnan Hasan

Member
Location
baghdad, Iraq
Branch circuit and International Code Council (ICC)

Branch circuit and International Code Council (ICC)

[h=3]chapter 36- International code council (ICC)[/h]Branch circuits in dwell- ing units shall supply only loads within that dwelling unit or loads associated only with that dwelling unit.
this is what ICC says. I need reference code in NEC
 

jumper

Senior Member
[h=3]chapter 36- International code council (ICC)[/h]Branch circuits in dwell- ing units shall supply only loads within that dwelling unit or loads associated only with that dwelling unit.
this is what ICC says. I need reference code in NEC

210.25 Branch Circuits in Buildings with More Than
One Occupancy.
(A) Dwelling Unit Branch Circuits. Branch circuits in
each dwelling unit shall supply only loads within that dwelling
unit or loads associated only with that dwelling unit.
(B) Common Area Branch Circuits. Branch circuits installed
for the purpose of lighting, central alarm, signal, communications,
or other purposes for public or common areas of
a two-family dwelling, a multifamily dwelling, or a multioccupancy
building shall not be supplied from equipment that
supplies an individual dwelling unit or tenant space.
 

Adnan Hasan

Member
Location
baghdad, Iraq
210.25 Branch Circuits in Buildings with More Than
One Occupancy.
(A) Dwelling Unit Branch Circuits. Branch circuits in
each dwelling unit shall supply only loads within that dwelling
unit or loads associated only with that dwelling unit.
(B) Common Area Branch Circuits. Branch circuits installed
for the purpose of lighting, central alarm, signal, communications,
or other purposes for public or common areas of
a two-family dwelling, a multifamily dwelling, or a multioccupancy
building shall not be supplied from equipment that
supplies an individual dwelling unit or tenant space.
thank you.
what about my Q2?
 

Adnan Hasan

Member
Location
baghdad, Iraq
210.25 Branch Circuits in Buildings with More Than
One Occupancy.
(A) Dwelling Unit Branch Circuits. Branch circuits in
each dwelling unit shall supply only loads within that dwelling
unit or loads associated only with that dwelling unit.
(B) Common Area Branch Circuits. Branch circuits installed
for the purpose of lighting, central alarm, signal, communications,
or other purposes for public or common areas of
a two-family dwelling, a multifamily dwelling, or a multioccupancy
building shall not be supplied from equipment that
supplies an individual dwelling unit or tenant space.

Assuming each unit has integral overload protection or such and a disconnecting means, yes-if the circuit is properly sized.
many thanks
 

kwired

Electron manager
Location
NE Nebraska
Assuming each unit has integral overload protection or such and a disconnecting means, yes-if the circuit is properly sized.

See 430.53.

An 800 watt motor @ 230 volts is getting close to pushing the limits here, especially if there are to be 5 units on the circuit, but depending on exactly what its ratings are it may be fine.
 