Leo1
Member
- Location
- Los Alamos, NM
Is it required, or good practice, to drive a couple ground rods at the PV array disconnect switch, especially is the PV array and disconnect is not close to the utility tie-in ? [Because large arrays make for a large metal target it seems reasonable to reduce the travel of a lightning strike to local ground rods versus having the strike travel solely a couple hundred feet back to the utility earth ground.]
This would be in addition to ground rods at the first utility disconnect switch per NEC, and an equipment grounding conductor that is run with the new conductors from the PV system tie-in disconnect to the PV array and disconnect.