Jps1006

Member
Location
Northern IL
We have a project that is looking to put general duty 120-volt receptacles peppered throughout a field starting roughly 750' from a 480-volt source, then continuing for another 300-400 ft. Is anyone aware of an all-in-one 480 to 120 2-5KVA unit that I could feed with 480-volt at each location, with built-in transformer, disconnect and GFI to get 120-volt receptacle power?

The engineer has spec.'d #2 to the 120-volt 20-amp GFI locations fed form a 480 - 120/208 transformer in the field. We estimate we could do this in #10 if we could put smaller transformers at the point of use. I imagine this is a common problem with distances on sprawling sites.
 

tom baker

First Chief Moderator
Staff member
I have used Sq D Mini Power Zones - primary, transformer, secondary panel all in one post mountable enclosure, NEMA 3R. Seems like smallest is a 5 KW. With 5 KW you have some room for other loads
 

Jps1006

Member
Location
Northern IL
Thanks guys. We looked into it and the cost savings just aren't there. We are staying with one large transformer and over-sized cables everywhere.
 

masterinbama

Senior Member
I have used some smaller units for single receptacles tapped ahead of rooftop unit disconnects. They were listed for that application but I can't remember if there were any other listings.
 