There are a couple cases in article 220 where they specify the load you are required to use for a given purpose such as for a signage circuit (1200 VA) and for show window receptacles (75 va/ft) etc. These loads by their nature obviously run continuously (greater then 3 hours). In my load calcs, I have always taken these loads at face value and never bothered taking them at 125% because I assumed that when they wrote the NEC it was understood that these loads would run continuously.
I received 2 rejections within 6 months requesting that I take these loads at 125%. I didn't bother arguing with the plan reviewer because it represented such a small load. My question is, if the NEC gives you a fixed VA, should you still apply the demand factor of 125%?
I received 2 rejections within 6 months requesting that I take these loads at 125%. I didn't bother arguing with the plan reviewer because it represented such a small load. My question is, if the NEC gives you a fixed VA, should you still apply the demand factor of 125%?