Underground Duct Bank and Frost Line

Status
Not open for further replies.

faresos

Senior Member
I was told the underground ductbank needs to be below frost line.

1. Where is the requirement came from?
2. How critical to follow this requirement?
3. What is the rational for this requirement?

I?m working on a project that the frost line is approximately 60? .

Thanks,
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I would expect that it is a design spec. Two reasons come to mind. To pevent damage from the frost heave that can occur if you are not below the frost line and to prevent the water from damaging the conductors when it freezes and expands by 10%.
 