jdhaze

Member
Location
Birmingham, AL
Is there a table showing the maximum flash hazard boundary for the different hazard levels? What I'm trying to say is @ 1.2 cal/cm2 the distance is X, at 4 cal/cm2 the distance is Y, 8 cal....25cal.......?

thanks
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Is there a table showing the maximum flash hazard boundary for the different hazard levels? What I'm trying to say is @ 1.2 cal/cm2 the distance is X, at 4 cal/cm2 the distance is Y, 8 cal....25cal.......?

thanks

Unfortunately not as simple as that in real life. For a point source of energy (like a light bulb or a short arc) the energy per unit area falls off as one over the square of the distance. So at twice the distance the cal/cm2 will be 1/4. But if the energy source is not a point (say an arc uniform over a 2' by 2' area, for example) the energy can be focused in a particular direction and not drop off as fast over short (order of 5 feet) distances. And at high voltages the arc itself can extend over a variable region of space.

You can generalize more accurately when large distances from the arc flash (tens of feet) are involved, but I am not sure how useful that would be, since you would then be in the range of remote actuation anyway.
 
Last edited:

jdhaze

Member
Location
Birmingham, AL
Arc-Flash Maximum Boundary

Let see if I can understand. It sounds like you are bringing up the differences between open air flash vs. 'arc in a box'. Your other statement indicates that if you have 1.2cal/cm2 @ 18", the maximum arc-flash boundary will change if it is 480v vs. 4160v, is this an accurate assessment?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Let see if I can understand. It sounds like you are bringing up the differences between open air flash vs. 'arc in a box'. Your other statement indicates that if you have 1.2cal/cm2 @ 18", the maximum arc-flash boundary will change if it is 480v vs. 4160v, is this an accurate assessment?
That is an accurate assessment of what I said. I make no claim that what I said is accurate, and will wait for one of the regulars who deal in this all the time to comment. I would however correct "will change" to "may change"
 