p real
Member
- Location
- Fort Collins, CO
hello all, so recently completed installation of 100 amp panel to detached garage. Now to clarify, garage panel is fed from outdoor mdp that is also servicing the house associated with aforementioned garage. Ran #2 aluminum urd (dual rated rhw,rhw2) in pvc 1 1/4 conduit that went into an underground trench to the garage and proper egc. Put 100 amp breaker at mdp and on garage panel, separate grd rods and so forth. The inspector failed me because he says that rhw2 is only good for 90 amps under those conditions. I understand where he is getting that from because even tho the wire is rated for 90 degrees the breakers areonly good for 75 degrees but how is it that this garage is not being considered a separate building and the wires going to it should be considered residential feeders under 310.15b(7) and table 310.15b(7) am i wrong?