New GFI with a Dead Short

Status
Not open for further replies.

mkgrady

Senior Member
Location
Massachusetts
I turned on a new circuit that included a feed to a brand new P&S GFI. The breaker tripped immediatley. I went to a JB and isolated the part of the circuit that had the short and went to work trying to figure out how to replace the piece of romex. I assumed somebody ran a screw into the wire. I finally thought to make sure the short was not internal to the GFI and to my surprise it was. Anybody else ever run into this?
 

jeremysterling

Senior Member
Location
Austin, TX
I turned on a new circuit..(and t)he breaker tripped immediately. Anybody else ever run into this?

What I quoted of you I've experienced many times with brand new SQD QOB breakers with no actual fault. I always cycle these breakers several times prior to commissioning. Are you sure your GFCI actually has a fault or could it be first time jitters for the breaker?
 

p real

Member
Location
Fort Collins, CO
i have not seen a gfci ever trip a breaker before itself, but every single p and s tr gfi that i put in, if you set it first, and then energize it, it immediately trips and you hear a little momentary buzzing at that second between it being energized and it tripping, almost like a fuse link that burns out to show if it has ever been energized because it onlydoes it the first time you energize a brand new one. Maybe your little fuse didnt burn out like it was sposed to... Anybody else noticed this? It does it on every single one, but only the pand s ones.
 

sparkyrick

Senior Member
Location
Appleton, Wi
I turned on a new circuit that included a feed to a brand new P&S GFI. The breaker tripped immediatley. I went to a JB and isolated the part of the circuit that had the short and went to work trying to figure out how to replace the piece of romex. I assumed somebody ran a screw into the wire. I finally thought to make sure the short was not internal to the GFI and to my surprise it was. Anybody else ever run into this?

I had a service call a few months ago in a commercial kitchen to fix a problem with a dead short on a circuit. Turned out to be a P&S GFI failing as a dead short. No, it wasn't new, but it wasn't used that often either, looked almost new. No external signs of charring or melting either, it just failed. And no, I didn't bother to take it apart to see why it failed.
 

mkgrady

Senior Member
Location
Massachusetts
I didn't check the date of manufacture of the gfi receptacle. I returned it this morning and did not take it apart. I will ask the supply house guy if he will give it back and I will try to take it apart.

I have noticed the P&S gfi recepts do have a weird buzzing that sometimes goes on when you first turn it on. I don't remember a pattern to when it happens but I will start to pay attention to that.

You guys have confirmed to me that a shorted gfi recept is pretty rare out of the box. Thanks to all.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Seems to me I remember tracking down the same problem once. I don't remember the event.

I've also seen GFCIs that had no power at the face of the device when energized, but worked perfectly on the load side.

I guess that's why we hot check! :)
 

kwired

Electron manager
Location
NE Nebraska
i have not seen a gfci ever trip a breaker before itself, but every single p and s tr gfi that i put in, if you set it first, and then energize it, it immediately trips and you hear a little momentary buzzing at that second between it being energized and it tripping, almost like a fuse link that burns out to show if it has ever been energized because it onlydoes it the first time you energize a brand new one. Maybe your little fuse didnt burn out like it was sposed to... Anybody else noticed this? It does it on every single one, but only the pand s ones.

I don't know for certain, but I think the reason they trip is because of newer listing requirements for miswiring protection. There is some kind of latching relay that must have power when you reset it to remain latched. If it is reset with no power applied it will trip upon energization. This way if line/load are reversed it will not latch when resetting, and they are likely leave the factory in a tripped condition meaning power needs applied before they will reset. I have kind of come to this conclusion on my own and it is not something I can say I definitely am certain about. I do not know exactly what causes the buzzing sound, but have heard it myself many times.
 