maxamps
Member
- Location
- New Orleans
When installing a 1200 amp 3 phase Transfer Switch, between incoming service and the main service disconnect (1200 amp 3 phase 480 volt breaker, 4 wire system). Contractor is proposing 4 parallel runs of 350 mcm or 3 parallel runs of 600 mcm 90 degree conductors THHN and 90 degree terminals. My calculations are 1120 and 1140 amps respectively considering de-rating for the 4th current carrying conductor (the neutral). Would either of these be sufficient to supply the 1200 amp main switch, using the next size overcurrent device as exampled in section Article 240.4 (C) ?