PVC vs Rigid conduit in UG Duct Banks

Status
Not open for further replies.

Lenz81

Member
Location
Alaska
I am currently on job and they require to use Rigid Elbows for UG duct banks ,when i ask for reason nobody seems to have answer , is there any code or reuirement on using rigid elbows ? Installating Rigid elbow is very time consuming specially in case of bigger conduits .
Thanks
Lenz
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
RMC elbows are sometimes installed to prevent elbow damage that can be caused by the pulling rope when PVC elbows are used. A metallic elbow in a run of PVC must be at least 18" below grade to the top of the elbow.
 