Feed Thru Lug Panel

Status
Not open for further replies.

dav5y

Member
Location
NYC
Hi All,

I have a question, If I have a 400 amp riser feeding 225amp (main bkr) w/ feed thru lugs panels on the basement, first and second floors. Does the bus rating for the 225amp panels need to be 400 Amps ???? Im trying to avoid trough w/ a tap to the panel.......
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the bus is on the load side of the 225 amp CB then it only needs to have a minimum rating of 225 amps.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Thank you..... One more question tho... The lugs would have to be rated for 400 amps ????

Yes and no. To the extent that the lugs actually carry the feed-through current. At least up to the next-to-last panel.
The connections to the wires have to be able to carry the full current safely.
 
You could "drop off" amperage at each floor. Do a load calculation for each floor. Let's say it came to 100A per floor.

The first panel would have a 400A MB, 400A busses and 400A feed thru lugs. The second panel could have 300A ratings for MB, busses and FT lugs. The third panel 200A and so on.

In my example, you may even be able to use the tap rules and use 300A wire and lugs between the 400A panel and the 300A panel. And so on down the chain.
 