Transformer sizing for single phase motor

Status
Not open for further replies.

Alan K

New member
.5 HP pump, 230Volts, Single phase, Full load Amps=8.5, Locked Roter Amps= 30.1A, NEMA Start code "R"

Primary voltage is 480V. What size single phase transformer required for this pump?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
.5 HP pump, 230Volts, Single phase, Full load Amps=8.5, Locked Roter Amps= 30.1A, NEMA Start code "R"

Primary voltage is 480V. What size single phase transformer required for this pump?
Gross rule of thumb: minimum transformer kVA = 3X the motor HP value if there is nothing else on the circuit and starting across-the-line. So your motor is 1/2HP, use a 1.5kVA transformer minimum.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
130525-0906 EDT

Alan K:

0.5 HP 230 V and full load = 8.5 A looks wrong. VA = 1955. 0.5 HP output = 746/2 = 373 W. If you assume 85% efficiency and 0.8 PF, then VA = 550. A 1/2 Hp Sears motor of mine at 230 is labeled 4.3 A, or 989 VA. Are you reading the the 115 V full load amperes?

.
 
Status