Can i get a code section that says that. i just got turned down because no bushing on a ser connector. SER cable the inspector was unsure as well

300.4(G). An SE connector is not a raceway.

3300.4(G) Insulated Fittings. Where raceways contain 4 AWG
or larger insulated circuit conductors, and these conductors
enter a cabinet, a box, an enclosure, or a raceway, the con-
ductors shall be protected by an identified fitting providing
a smoothly rounded insulating surface, unless the conduc-
tors are separated from the fitting or raceway by identified
insulating material that is securely fastened in place.
Exception:
Where threaded hubs or bosses that are an
integral part of a cabinet, box, enclosure, or raceway pro-
vide a smoothly rounded or flared entry for conductors.
Conduit bushings constructed wholly of insulating ma-
terial shall not be used to secure a fitting or raceway. The
insulating fitting or insulating material shall have a tem-
perature rating not less than the insulation temperature rat-
ing of the installed conductors
 

Daja7

Senior Member
300.4(G). An SE connector is not a raceway.

thanks. what about an SER cable entering a PVC sleeve with male adapter. We always use bushings on threaded fittings but just curious if it would be required due to the jacket being an insulating protective material.
 