Can't you use the 75 degree column for SER as long as its not in insulation which then I know you must use the 60degree column? I don't see the article saying you can though, 2008 NEC.
The 2008 NEC does not allow the use of 75C. Art. 338.10(B)(4) states to go to Art. 334 part II-- that's for NM and we know that is 60C. The 2011 changed to 75C if not in insulation, etc
Oh ok in 2011 it changed. Where in the 2011 does it say 75degree is allowed?
I don't see where it says you can use the 75 degree columnAs stupid as this requirement sounds Dennis is correct. For the 2011 it in 338.10(B)(4).
It doesn't, it says that if not within insulation then you do not need to use the 60? C ampacity .
Well I don't see that specifically but I guess by it saying "shall comply with the installation requirements of part two of article 334 excluding 334.80" makes it ok?