Here is my wild guess of a solution.
Your total loop length is 2*690 = about 1400 ft.
A ballpark figure for full load current is 746 /240 = 3.1 A. 746 = 1 HP and using that as a ballpark for a 3/4 HP to account for inefficiency and PF may be low, but this I will compensate for by over estimating peak inrush at 10 times running load.
So that is 30 A at startup.
An A. O. Smith B642 3/4 HP 230 V motor is rated about 4.6 A full load. About 30% higher than my wild guess.
If we assume you really have 240 normally and don't want more than 20 V drop at startup, then maximum wire resistance would be 20/30 = 0.67 ohms. #6 is about 0.4 ohms per 1000 ft or about 0.56 ohms for your loop length. I think this is larger than what you really need for several reasons.
You need to know what your nominal voltage really is.
You need to know what a realistic maximum series resistance is for motor startup with your normally expected minimum nominal voltage. This will determine your wire size. In a long run like this running current is not a factor. So motor performance at startup is the criteria. Your motor running load will not overheat the wire under run conditions, because voltage drop under startup is the dominate criteria.