Conduit typer for Riser?

Status
Not open for further replies.

Benton

Senior Member
Location
Louisiana
Hi,

I'm trying to find in code what option I have for conduit on my overhead riser. Could someone guide me in the right direction? Can I use PVC, or EMT?
 

Rewire

Senior Member
you may want to check with your POCO ours sets out their requirements 2 in rigid is minimum if you attach to it, emt and pvc are allowed only if you house knob Thet require the service to be in conduit.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
you may want to check with your POCO ours sets out their requirements 2 in rigid is minimum if you attach to it, emt and pvc are allowed only if you house knob Thet require the service to be in conduit.

I understood the first few words here, but "Google Translate" couldn't even touch the rest of the last sentence. :p:?:lol:
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Here's the relevant NEC section. As previously stated it makes no mention of size or type of conduit.

230.28 Service Masts as Supports. Where a service mast
is used for the support of service-drop conductors, it shall
be of adequate strength or be supported by braces or guys
to withstand safely the strain imposed by the service drop.
Where raceway-type service masts are used, all raceway
fittings shall be identified for use with service masts. Only
power service-drop conductors shall be permitted to be at-
tached to a service mast.
 

Benton

Senior Member
Location
Louisiana
Thanks guys! I will definitely have to talk with POCO. I have a piece of angle iron for support so I should be ok, but better safe than sorry.
 