Additional ground rod for seprate panel over 20 AMPs

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I know of NO addition of the NEC that ever had such a "blanket" requirement fro sub-panels.
A sub-panel in a separate building does require a grounding electrode system per 250.32 which is a current requirement.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
In previous edition of the NEC a sub panel with a circuit more then 20 AMPs was required to have its own ground rod. Does this still apply.

I'm not sure if this ever was true regarding the NEC. As Augie stated a panelboard in a separate structure will require connection to a GES. That could be other electrodes besides two ground rods.
 