430.6(A) Exception 2: For equipment that employs a shaded pole or permanent split capacitor type fan or blower motor THAT IS MARKED WITH MOTOR TYPE, the full load current for such motor marked on the nameplate of the equipment in which the fan or blower motor is employed shall be used instead of the instead of the horsepower rating to determine the ampacity, branch circuit conductors, ocpd....This marking on the nameplate shall not be less than the current marked on the fan or blower motor nameplate.
Not sure what is going on here. I have a Condensing unit that has a condensor fan attached to it. It is a 1/6th HP fan with a nameplate that say 1.1A. I am pretty sure that it must be a PSC motor, or even a shaded pole motor. The NEC tables gives me 2.2A for such a motor (at 230V). Does this exception apply to my condensing unit?