SEC (Again)

Status
Not open for further replies.

tonype

Senior Member
Location
New Jersey
Common thread with me - however, each one is just a little different (or so I perceive). Messenger wire is the only support for the SEC from the service mast down to the wall below the roof skirt. Am I correct that the SEC should be supported no more than 6 feet apart. What about the wrap around the gutter? DSCF8049_edited-1.jpg
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
SE cable should be supported as NM cable- 4 1/2" and within 12" of the fitting. This install is an embarrassment and should never have been allowed
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
A strap or two and secure the weatherhead to the fascia and you're good to go. Going around the gutter is a somewhat common installation around here.
 