Maybe it is the definition of words that are confusing, but the bond between the grounded conductor and the frame of the generator is typically determined from 250.66. If the equivelent ungrounded conductor is larger than 1100kCMIL copper, when is the bond chosen at 3/0AWG per the table and when is it chosen at 12-1/2% per 250.28(D)(1)?