Cooktop and wall over single circuit

Status
Not open for further replies.

electricblue

Senior Member
Location
Largo, Florida
Occupation
EC
Am I right on this? I got a 4 kw oven and 7.6kw cooktop. 240v. So total is 11.6kw. Column C say 8 percent derate. After I derate the circuit it's 44.46 amps. We can put this on the old 50amp range wire.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
For some reason this table is hard for people to understand. Col A and B are percent but Col C is KW. There are some many factors to look at but in your case Note 4 comes into play so you consider the 2 units as a single unit and then use Col C
 