Motor-1 needs 50A feeder (480V,3PH, 3#6, 1#10 Ground, 3/4" EMT) and 50A/3P CB protection - circuit #1.
Motor-2 needs 15A feeder (480V, 3PH, 3#12, 1#12 Ground, 3/4" EMT) and 15A/3P CB protection - circuit #2.
Both motors are fed from same panel, the panel is located around 200' from motor #1 and 150' from motor #2.
(Both motors are located in the same area.)
We made a mistake on paper and have motor #1 fed out of circuit #2 and vice versa and contractor installed that way.
Solution #1
Swap 50A and 15A breaker location in panel, leave 50A feeder to serve motor #2.
Re-use existing conduit to motor #1 and re-pull new wires (#6, #10G) to feed it.
Solution #2
Install a j-box near motor #1 location, intercept 15A feeder and extend feeder to motor #2.
Install a j-box near motor #2 location, intercept 60A feeder and extend feeder to motor #1.
Does anyone has better solutions for this and minimize labor cost, etc? Thanks.
Motor-2 needs 15A feeder (480V, 3PH, 3#12, 1#12 Ground, 3/4" EMT) and 15A/3P CB protection - circuit #2.
Both motors are fed from same panel, the panel is located around 200' from motor #1 and 150' from motor #2.
(Both motors are located in the same area.)
We made a mistake on paper and have motor #1 fed out of circuit #2 and vice versa and contractor installed that way.
Solution #1
Swap 50A and 15A breaker location in panel, leave 50A feeder to serve motor #2.
Re-use existing conduit to motor #1 and re-pull new wires (#6, #10G) to feed it.
Solution #2
Install a j-box near motor #1 location, intercept 15A feeder and extend feeder to motor #2.
Install a j-box near motor #2 location, intercept 60A feeder and extend feeder to motor #1.
Does anyone has better solutions for this and minimize labor cost, etc? Thanks.