Type UF Ampacity

Status
Not open for further replies.

c_picard

Senior Member
Location
USA
340.80 Ampacity. The ampacity of Type UF cable shall be
that of 60?C (140?F) conductors in accordance with 310.15.

340.112 Insulation. The conductors of Type UF shall be
one of the moisture-resistant types listed in Table
310.104(A) that is suitable for branch-circuit wiring or one
that is identified for such use. Where installed as a substitute
wiring method for NM cable, the conductor insulation
shall be rated 90?C (194?F).

Question: When selecting conductor size for a branch circuit, using UF as a substitute for NM, the UF must be constructed using 90deg conductors, and I use the ampacity listed in the 60deg column. Correct?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I agree with Roger but will add that if derating is involved you may use the 90C rating as long as the final ampacity used is not larger than the 60C rating
 

c_picard

Senior Member
Location
USA
Right, the same way one would be able to use the 90C column so long as the resulting ampacity did not exceed the 75C column for terminal ratings.
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
I've never seen in explicitly in the code, but modern UF is typically labeled UF-B (just like NM and NM-B). I'm assuming this means it is 90C rated (for derating purposes only), but the book doesn't say that like it does for NM.
 

jumper

Senior Member
IIRC neither NM-B and UF-B is a recognized NEC designation, the "-B" just means that it means it was manufactured under modern code as having 90C conductors-else you have the old style 60C stuff.

A UL thing I guess.
 

kwired

Electron manager
Location
NE Nebraska
IIRC neither NM-B and UF-B is a recognized NEC designation, the "-B" just means that it means it was manufactured under modern code as having 90C conductors-else you have the old style 60C stuff.

A UL thing I guess.
NEC does mention NM-B in the informational note after 334.112, and basically says any cable marked NM-B meets the 90C requirement for conductor insulation mentioned in 334.112.
 