340.80 Ampacity. The ampacity of Type UF cable shall be
that of 60?C (140?F) conductors in accordance with 310.15.
340.112 Insulation. The conductors of Type UF shall be
one of the moisture-resistant types listed in Table
310.104(A) that is suitable for branch-circuit wiring or one
that is identified for such use. Where installed as a substitute
wiring method for NM cable, the conductor insulation
shall be rated 90?C (194?F).
Question: When selecting conductor size for a branch circuit, using UF as a substitute for NM, the UF must be constructed using 90deg conductors, and I use the ampacity listed in the 60deg column. Correct?