Transfer Switch

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Utility transformer where the secondary would be a service, definitely not unless the TS is 'service rated'.

Feeder transformer, I would like to say no, but IMO, 240.21(C)(2) would allow it, but only under the 10 ft rule which allows termination in a 'device' rather than overcurrent devices.
 