- Location
- Tennessee NEC:2017
- Occupation
- Semi-Retired Electrician
I didn't intend to say same thing you said in red above. If generator doesn't have a N-G bond but does have a GFCI, where is the unbalanced current going to flow to make it trip? Even a line to ground fault will not trip the GFCI as the return path will be through the GFCI neutral and should be equal magnitude as the "hot" conductor. If it does have a N-G bond then neutral current will split over the grounded and grounding conductors causing imbalance through GFCI and then it will trip.
I didn't say if it had one and not the other. I said if the genny was bonded, the device wouldn't work because the service would already be bonded, and would trip the genny's GFCI. It would be hard to trip a GFCI if there wasn't one on the genny. I understand how a GFCI works, I was just stating what the website instructions said.
Maybe if I (or the instructions) would have said: "if the generator is installed as a SDS, then the device/transfer switch wouldn't work because it doesn't switch the neutral, and assuming the genny also has a GFCI, it would trip."
Would that have been more clear?