Derating discussion

Status
Not open for further replies.

MBerner

Member
Location
Burbank, CA USA
I have been discussing the derating factor for 12 gagewire. The way I read the NEC is, 3 or more current carrying conductors usetable 316. Well I see #12 wire is rated for 30 amps at 90'. And the asteriskfor 20 amps is for over current protection only. So at 70% of 30 amps which is21 amps I can run 7 to 9 # 12s in a conduit, right???
 

kwired

Electron manager
Location
NE Nebraska
I have been discussing the derating factor for 12 gagewire. The way I read the NEC is, 3 or more current carrying conductors usetable 316. Well I see #12 wire is rated for 30 amps at 90'. And the asteriskfor 20 amps is for over current protection only. So at 70% of 30 amps which is21 amps I can run 7 to 9 # 12s in a conduit, right???

As long as no additional derating is necessary (like for ambient temperature) then yes.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
And to clarify one step further, you only get to start at the 90C column if the conductor's insulation system is shown at the top of that column. For example, a #12 type THHN would be derated from the 90C value of 30 amps. A #12 type THWN would be derated from the 75C value of 25 amps. The code article that allows this is 110.14(C).
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
And to clarify one step further, you only get to start at the 90C column if the conductor's insulation system is shown at the top of that column. For example, a #12 type THHN would be derated from the 90C value of 30 amps. A #12 type THWN would be derated from the 75C value of 25 amps. The code article that allows this is 110.14(C).


That is very correct and an a$$ biter. If the conductor runs through any wet location and the inside of conduit in a wet location is a wet location then you have to use the THWN conductor rating. Bet this has been violated a few times! (by me:eek:hmy:!)
 

MBerner

Member
Location
Burbank, CA USA
Thanks, Strathead, charlie b , mwm1752, kwired and cowboyjwc. And cowboyjwc, "And don't forget the terminal ratings too. If the terminals are rated 75 degrees then that's the highest table you can use." I did not know that that was a factor. Thanks.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Thanks, Strathead, charlie b , mwm1752, kwired and cowboyjwc. And cowboyjwc, "And don't forget the terminal ratings too. If the terminals are rated 75 degrees then that's the highest table you can use." I did not know that that was a factor. Thanks.

To expand on Rob's statement, if the terminals are rated for 75 degrees, that is the highest amount of current you can allow the wire to carry. It doesn't have anything to do with the temperature rating of the conductor's insulation. The number of current carrying conductors and the ambient temperature considerations are used to determine the derating, based on the ampacity of the conductor, and then, if the allowable ampacity is still higher than that of the terminations, then you must select the column that matches the terminations for the allowable temperature.
 

sandsnow

Senior Member
That is very correct and an a$$ biter. If the conductor runs through any wet location and the inside of conduit in a wet location is a wet location then you have to use the THWN conductor rating. Bet this has been violated a few times! (by me:eek:hmy:!)

I thought all the manufacturers were producing THWN-2. The "-2" gives you the extra kick up to 90 degree rating for wet locations. I'll take a peek when I'm out today at what's being used around here.
 

kwired

Electron manager
Location
NE Nebraska
I thought all the manufacturers were producing THWN-2. The "-2" gives you the extra kick up to 90 degree rating for wet locations. I'll take a peek when I'm out today at what's being used around here.

I think that is what you will mostly find, but will not promise you will never see any without the -2 rating.
 

Fliz

Member
Location
San Francisco
Big question. Say you have a 60 degree terminal (they exist) and you were running a 60 amp circuit. #6 75 degree wire is good for 60 amps right? Right. Of course you cannot run a #6 wire off a 60 degree terminal for a 60 amp circuit, because the terminal is not good for it.

Now, here's my question. You run a #4 wire off the 60 degree terminal to a junction box and it is spliced to a #6 75 degree wire and the rest of the circuit run on #6 (to presumably another terminal that is rated at 75 degrees). If no other derating factors are needed, is this code compliant?



This falls under the "derating discussion" topic but not specific to the OP.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Big question. Say you have a 60 degree terminal (they exist) and you were running a 60 amp circuit. #6 75 degree wire is good for 60 amps right? Right. Of course you cannot run a #6 wire off a 60 degree terminal for a 60 amp circuit, because the terminal is not good for it.

Now, here's my question. You run a #4 wire off the 60 degree terminal to a junction box and it is spliced to a #6 75 degree wire and the rest of the circuit run on #6 (to presumably another terminal that is rated at 75 degrees). If no other derating factors are needed, is this code compliant?
Yes it is.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Big question. Say you have a 60 degree terminal (they exist) and you were running a 60 amp circuit. #6 75 degree wire is good for 60 amps right? Right. Of course you cannot run a #6 wire off a 60 degree terminal for a 60 amp circuit, because the terminal is not good for it.

Now, here's my question. You run a #4 wire off the 60 degree terminal to a junction box and it is spliced to a #6 75 degree wire and the rest of the circuit run on #6 (to presumably another terminal that is rated at 75 degrees). If no other derating factors are needed, is this code compliant?



This falls under the "derating discussion" topic but not specific to the OP.

To muddy the waters a little more a #6 AWG at 60? C is rated at 55 amps. If your connected load is 55 amps or less you can go up to the next standard size OCPD which is 60 amps so you would even need to splice on the #4. :)

But yes you can do what you've suggested when trying to work with a 60? C terminal.
 