Not open for further replies.

apelk

Member
Location
Houston, TX
Hello, seeing as though I sit at a desk and design all day while not getting out enough to see how things are actually installed, I am curious as to how one mounts a receptacle (and also the conduit running down to the device) within a CMU wall . Anyone have a sketch or CAD detail they would share? I'm more a visual learner. What would be the difference between new construction and an existing wall?

The client is putting up some rack shelving units against a wall and doesn't want receptacles to force the shelving away from the wall. Of course, this installation requires a weatherproof cover, so that's going to jut out a couple inches from the wall anyway.

Comments?
 

iwire

Moderator
Staff member
Location
Massachusetts
There are many ways but we often use these kinds of boxes

63895.jpg


The mason cuts a hole for them and uses mortor to secure them.

The pipe is usally not supported
 