Feeders and Branch Circuits in Wireway

Status
Not open for further replies.

Duncan8943

Member
Location
Lexington
I've got a possible situation where I may need to have both main panel feeders and branch circuits in the same 6"x6" wireway. Normally, I don't practice mixing the two in the same wireway. Are there any code issues with this?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
As long as you don't mix service conductors with any other feeders or circuits in the same raceway then there is no issue.
 