Arc Fault requirements in Ohio

Status
Not open for further replies.

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
How small does any gap need to be to stop calling it an arc and start calling it a high resistance connection?
That seems pretty clear cut. If it is a gas-tight connection, there cannot be an arc although there may be a high resistance if the contact area is small enough. But enough pressure for gas-tight would deform the copper enough to provide some area.
If it is a metal-to-metal connection which will carry current at low voltage, then it is a high resistance connection. If the current flow does not start until you go above a voltage threshold, then it is an arc. Or a diode. You can make a very low voltage copper-oxide rectifier from a wire and another piece of metal if you try hard enough.
 