here's a screwy question for you.

you have 2 ten HP motors on the same feeder.

14X2.5 = 35A.

So 35A is the maximum OCPD that can provide SC protection to the motors.

What allows you to feed both motor controllers with the same 35A feeder breaker?

and what do you size the conductor ampacity at?

there are no downstream CBs. so the feeder has to be sized to the ampacity of the conductors, right?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
what does it actually say.

the stuff after it in brackets is explanatory - it just tells you where the maximum value of the motor OCPD can be found.

it also does not require you to use a standard size CB. If the number came out to 85.2, you could use an 85.2A CB if you could find one.

I disagree. You are choosing to ignore "based on the maximum permitted value." If your view was correct, they could just leave the part in the brackets out. Its superfluous.

Consider two feeders with identical motors. One had a 70A, 20A and 20A branch c/b...and the other a 60A, 20A and 20A branch c/b. The feeder conductors would be the same size, the full load current on both feeders would be the same size, the motor overloads on each motor would be the same size. Why would one require a smaller feeder c/b?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
here's a screwy question for you.

you have 2 ten HP motors on the same feeder.

14X2.5 = 35A.

So 35A is the maximum OCPD that can provide SC protection to the motors.

What allows you to feed both motor controllers with the same 35A feeder breaker?

and what do you size the conductor ampacity at?

there are no downstream CBs. so the feeder has to be sized to the ampacity of the conductors, right?

I'm not sure where your going with this, but let's start with the most obvious...

you have 2 ten HP motors on the same feeder...

there are no downstream CBs.

If there are no downstream CBs, then you have a branch circuit, not a feeder.

14X2.5 = 35A.

So 35A is the maximum OCPD that can provide SC protection to the motors.

14x2.5 + 14 = 49, so 45A is maximum OCPD that can provide SC protection to the feeder. Each motor would need its own branch circuit SC protection.

and what do you size the conductor ampacity at?

The feeder conductors would need an ampacity of at least 14x1.25 + 14 = 32A, or #10AWG.

Each branch circuit could be supplied by a #14AWG from the 35A branch OCPD.
 
Last edited:

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
here's a screwy question for you.

you have 2 ten HP motors on the same feeder...

there are no downstream CBs. so the feeder has to be sized to the ampacity of the conductors, right?

If you really wanted to consider two motors on the same branch circuit, lets consider two 15HP motors instead.

The max OCPD would be 21x2.5 = 52.5 => or a 60A breaker. This would fall under 450.53(B). (That section also requires that it be determined that the branch OCPD will not open under the most severe normal operating conditions.)

The conductor ampacity would have to be 21x1.25 + 21 = 47.3, or #8. So the branch OCPD can be larger than the ampacity of the conductors.
 
Last edited:

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I disagree. You are choosing to ignore "based on the maximum permitted value." If your view was correct, they could just leave the part in the brackets out. Its superfluous.

Consider two feeders with identical motors. One had a 70A, 20A and 20A branch c/b...and the other a 60A, 20A and 20A branch c/b. The feeder conductors would be the same size, the full load current on both feeders would be the same size, the motor overloads on each motor would be the same size. Why would one require a smaller feeder c/b?

i am ignoring it because it is explanatory in nature and not an allowance to use a larger value than is actually installed.

it isn't superfluous, it is explanatory.

its because the code says so. No good reason.
 
Last edited:

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
If you really wanted to consider two motors on the same branch circuit, lets consider two 15HP motors instead.

The max OCPD would be 21x2.5 = 52.5 => or a 60A breaker. This would fall under 450.53(B). (That section also requires that it be determined that the branch OCPD will not open under the most severe normal operating conditions.)

The conductor ampacity would have to be 21x1.25 + 21 = 47.3, or #8. So the branch OCPD can be larger than the ampacity of the conductors.

I still don't see where you are allowed to go up to the next std size CB.

450.53(B) is handy when you have two motors of the same size, and you are convinced that if you start them up simultaneously they won't trip, or you make it so they can't start simultaneously.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
i am ignoring it because it is explanatory in nature and not an allowance to use a larger value than is actually installed.

it isn't superfluous, it is explanatory.

its because the code says so. No good reason.

According to 90.5(C), explanatory material is included in Fine Print Notes. In addition, Brackets containing references to other NFPA documents are for informational purposes.

Since the bracketed text in 430.62 is neither a Fine Print Note nor a reference to another NFPA document, I would have to believe that it is not explanatory material, but part of the Code text.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I still don't see where you are allowed to go up to the next std size CB.

450.53(B) is handy when you have two motors of the same size, and you are convinced that if you start them up simultaneously they won't trip, or you make it so they can't start simultaneously.

450.53(B) says "IF the branch circuit short-circuit and ground-fault protective device is selected not to exceed 430.52 for the smallest rated motor..."

430.52 says the protective device (inverse c/b) shall not exceed 250% of the motor FLA, exception 1 lets you go up to the next standard rating.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
450.53(B) says "IF the branch circuit short-circuit and ground-fault protective device is selected not to exceed 430.52 for the smallest rated motor..."

430.52 says the protective device (inverse c/b) shall not exceed 250% of the motor FLA, exception 1 lets you go up to the next standard rating.

yea. I was still thinking of 430.62.

These multi-motor things make my head spin sometimes.

makes me glad for type F motor starters.
 

fifty60

Senior Member
Location
USA
Sorry for the headache's guys. So let me see if I understand. 215.3 is giving the MINIMUM feeder size that you can have, which is 125% of all the continuous loads motor or non motor. 430.62 and 430.63 is giving you the maximum size OCPD. So if I am using a D curve breaker sized at 125% of the largest motor load, and add all of the other loads together...and this is less than the value obtained by the method in 215.3, then I HAVE to use the value in 215.3. I can never have a feeder OCPD larger than 430.62-3 UNLESS that value is less than 215.3, then I have to use the rating obtained in 215.3.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Sorry for the headache's guys. So let me see if I understand. 215.3 is giving the MINIMUM feeder size that you can have, which is 125% of all the continuous loads motor or non motor. 430.62 and 430.63 is giving you the maximum size OCPD. So if I am using a D curve breaker sized at 125% of the largest motor load, and add all of the other loads together...and this is less than the value obtained by the method in 215.3, then I HAVE to use the value in 215.3. I can never have a feeder OCPD larger than 430.62-3 UNLESS that value is less than 215.3, then I have to use the rating obtained in 215.3.

you can have whatever size OCPD you want if you make the wires big enough.

this whole exercise is about making the OCPD as small as possible for the minimum wire size required.
 

fifty60

Senior Member
Location
USA
They can be whatever size, but they must be at least as big as the rating obtained in 215.3. 430.62-3 allows you to raise the size of the breaker whilst not raising the size of the conductor, and still be able to maintain the minimum conductor size pointed to by 430.62. Does that sound correct?

There is no situation where I can size teh motor OCPD close to the motor (like 125%) and then be able to use a feeder OCPD under the rating obtained from 215.3? Taking the motor only OCPD sized at 125% is going to be less than taking all of the loads multiplied by 125%...
 

fifty60

Senior Member
Location
USA
Can I use 430.63 to size my OCPD smaller than what is designated by 215.3? 125% of the largest motor plus all of the loads is smaller than 125% of all the loads.

It seems by the explanations here is that I can get my minimum feeder conductor size, which is 125% of largest motor, 100% of other motors, and 125% of everything else and then use an OCPD for that conductor in accordance with 430.63. If the OCPD rating is less than the ampacity of the above conductor then I can use it. But this is where I get confused...

215.3 is giving the MINIMUM i can use...does whatever I calculate in 430.63 have to be above this, or I am forced to default to the 215.3 value?

The advantage of 430.63, with my current understanding, is that you can size the OCPD larger than the ampacity of the feeder conductor within the confines of 430.63.
 