Redundant Ground in Hospital Grade MC cable

Status
Not open for further replies.

SigmaElec

Member
Location
Garner, NC
I was wondering what you do with the redundant ground when you are running hospital grade MC cable, do you homerun it back to the panel?

Thanks!
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I was wondering what you do with the redundant ground when you are running hospital grade MC cable, do you homerun it back to the panel?

Thanks!
Depends on whether is really is a "redundant" ground or they need to provide an "isolated" ground at some outlets. What you can or should do with the extra ground wire differs.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
In my opinion, 517.13 requires the "redundant" grounding conductor to be run back to the circuit's source.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Depends on whether is really is a "redundant" ground or they need to provide an "isolated" ground at some outlets. What you can or should do with the extra ground wire differs.
There is only one wire type EGC in HCFC, the aluminum runner is only for shunting the cable sheath along it's length and could be cut off at the connector. This leaves the metallic sheath as the only other EGC, no different than running EMT or metal conduit.

Roger
 