underground service trench depth

Status
Not open for further replies.

iand74

Member
The POCO I have worked with in the past requires a 30" trench for an underground service. I'm planning an underground service with a different POCO (National Grid) and they only require the trench to be NEC compliant.



As far as i can see NEC only requires 18" per 300.5. True?

Conductors will be in PVC
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Unless you are under a street, highway, road, driveway or parking lot.
 