Historical electrical code question: 1995

Status
Not open for further replies.

kgilfilen

Member
I have a home that was built in 1995, and I noticed that one of the two kitchen receptacle circuits (both 20A) is not protected by GFIs. It is the one furthest away from the sink. It also supplies the hood and refrigerator. Unfortunately, the fridge is at the end of the circuit, so I will have to put GFIs on the three countertop receptacles to bring it into current compliance. Does anyone know if it was a code violation in 1995 to not have GFI protected receptacles on kitchen counters? I am considering claiming that this is grandfathered in; I will still put in the GFIs, but I want credit for them.

Thanks, Kenny
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
In the 1993 NEC Section 210-8(5), 125V, 15 and 20A receptacles to serve counter top surfaces, installed within 6' of a kitchen sink, were required to have ground-fault circuit-interrupter protection for personnel.

(This changed in 1996 to say all countertop 125V, 15 and 20A receptacles in kitchens require gfci protection for personnel.)
 

Smart $

Esteemed Member
Location
Ohio
I don't have a 1993 edition to reference, but I'll go out on a limb and guess that only receptacles within 6' of the nearest sink edge were required to be GFCI-protected.

ETA: Typing while David was posting :)
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
I have a home that was built in 1995, and I noticed that one of the two kitchen receptacle circuits (both 20A) is not protected by GFIs. It is the one furthest away from the sink. It also supplies the hood and refrigerator. Unfortunately, the fridge is at the end of the circuit, so I will have to put GFIs on the three countertop receptacles to bring it into current compliance. Does anyone know if it was a code violation in 1995 to not have GFI protected receptacles on kitchen counters? I am considering claiming that this is grandfathered in; I will still put in the GFIs, but I want credit for them.

Thanks, Kenny
Maybe a dumb question but are the two outlets on the same circuit? In my house outlets in both bathrooms as well as outside by the front and back doors are all protected by one GFI in one of the bathroom outlets.
 

mgookin

Senior Member
Location
Fort Myers, FL
Built in 1995 does not mean under 1993 code. The date the permit is applied for controls what code applies. And it takes years to adopt a code by a local jurisdiction. I'd step back one more code unless you have the plans, permits, etc. And for sure back then anything >6' from sink did not require GFCI.
But isn't that fridge supposed to be a dedicated circuit?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Built in 1995 does not mean under 1993 code. The date the permit is applied for controls what code applies. And it takes years to adopt a code by a local jurisdiction. I'd step back one more code unless you have the plans, permits, etc. And for sure back then anything >6' from sink did not require GFCI.
But isn't that fridge supposed to be a dedicated circuit?

1987 & 1990 also required GFCI protection for 125V, 15 & 20A receptacles serving countertops WITHIN 6' of a kitchen sink.

There is no requirement for a fridge to be on a dedicated circuit.
 

kgilfilen

Member
In the 1993 NEC Section 210-8(5), 125V, 15 and 20A receptacles to serve counter top surfaces, installed within 6' of a kitchen sink, were required to have ground-fault circuit-interrupter protection for personnel.

(This changed in 1996 to say all countertop 125V, 15 and 20A receptacles in kitchens require gfci protection for personnel.)
Thanks, that explains it perfectly. This second circuit is definitely beyond 6 feet. I did all of my wiring in 2004-2009, so I never wired a kitchen without full GFI protection. And of course, I'd never put the fridge at the end of the circuit, much less on the same circuit with the other three countertop receptacles.
 
Last edited:

kgilfilen

Member
Maybe a dumb question but are the two outlets on the same circuit? In my house outlets in both bathrooms as well as outside by the front and back doors are all protected by one GFI in one of the bathroom outlets.
AFAIK, just the hood and fridge are on that circuit with the countertop receptacles.
 

iwire

Moderator
Staff member
Location
Massachusetts
Built in 1995 does not mean under 1993 code. The date the permit is applied for controls what code applies.

Good point depending on the area it could be under a older code.


And it takes years to adopt a code by a local jurisdiction.

That depends on the state, where I am the new code always takes effect 1/1 of the code cycle. So on 1/1/93 we would have been on the 93 code.
 

LEO2854

Esteemed Member
Location
Ma
It killed me to take my MA 15 hour continuing education class on the 2011 and not more than a month later I was taking a CT 7 hour class on the 2005. :(

Thankfully it's only 7 hours,,does that count for the extra 6 hours?
 

kwired

Electron manager
Location
NE Nebraska
Built in 1995 does not mean under 1993 code. The date the permit is applied for controls what code applies. And it takes years to adopt a code by a local jurisdiction. I'd step back one more code unless you have the plans, permits, etc. And for sure back then anything >6' from sink did not require GFCI.
But isn't that fridge supposed to be a dedicated circuit?

210.52(B)(1):

(B) Small Appliances.
(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.

Dedicated circuit is permitted but not required.

The range hood is not permitted on a SABC though.
 

kgilfilen

Member
210.52(B)(1):



Dedicated circuit is permitted but not required.

The range hood is not permitted on a SABC though.
Is that today's code, or 1995? Now I haven't seen electrical inspectors go through a house and map out circuits, but I would expect a house to be wired to current code for that jurisdiction. Again, I would have put the hood on a separate circuit, because they often get replaced with microwaves, and suddenly the circuit is close to being full. IIRC, I used to provide two kitchen receptacle circuits that were fully GFI protected, and served nothing but what the homeowner plugged into them on the countertop. The fridge and hood would be on one circuit, the dishwasher and disposal would each have their own breaker, but were co-located under the sink, the range would be on its own 220 branch, and then lights could be combined with other lighting.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Exceptions?

Exceptions?

Even if you pin down the code cycle for the house's construction, your jurisdiction may have had amendments which negated the requirement for GFCI's. You'd need to track down the enabling legislation to find out.
 