HoosierSparky
Senior Plans Examiner, MEP
- Location
- Scottsdale AZ
- Occupation
- Senior Plans Examiner
One of my buddies found this new electric service. It is a Sq D CU12L400CN. The single pole breakers at the top buss go to enclosed garage recepts and lights. The 2p 80 feeds a pool sub-panel. The 2p 30 feeds an A/C disconnect(non-fused). The contractor cannot understand why is installation is wrong. Can anyone else explain it to him?:blink: