Hendrix

Senior Member
Location
New England
Am I right in thinking that, since the pedistal is a structure as defined in the NEC, that the feeders to the house need a main disconnect because there will be more than 6 throws of the hand?
 

Npstewart

Senior Member
I think 225.32 would require a disconnect on the house and if you are talking about a panel which presumably has multiple breakers in it then you would need a GEC as well because you probably dont meet 250.32(A). IMO it probably wouldn't have to be fused though.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Also, keep in mind that the conductors from the meter/main combo are now a feeder (not service conductors) and so will require an EGC in addition to the neutral.
 