What is the best method to splice/extend a water bond wire that is aluminum?

Other than replacing the wire completely. At times when altering a service the wire is 1 ft too
short to reach.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Trevor was asking if it is a grounding electrode conductor because you cannot splice it unless you use an irreversible connector.
 

bth0mas20

Senior Member
Location
Maryland
I use t&b c taps that are crimped on to the gec and the inspectors are good with that as long as its accessible. However these are not rated for use with aluminum...copper only.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
That would work providing you have the proper crimping tool. If it's not the GEC you could use a split bolt.
 