so im still fairly new to the electrical trade since the end of 2011 and theres a lot im still learning and wanting to learn but my question is about the bonding of the neutral and ground in the electrical service. now ive been under the impression you only make this bond once in the service unless down the line a separately derived power source is installed. for example a transformer but other then that im clueless and ive looked it up in the code and the best article I could find was 250.24 in the 2011 nec. but it still didn't really answer my question on if u can make that bond more then once in one service? so I thought u guys could help me out with an answer and maybe a code reference if possible?
Hello...
Welcome to the forum and the electrical trade...:thumbsup:
250.24(A)(1) ..means that you are bonding your neutral and your grounding conductors at the service disconnect,your neutral must not be grounded anywhere else otherwise fault current will not trip the main disconnect or any of the other circuit breakers or fuses in the main panel.
Now in the case of a transformer creating a new service in a building such as a store in a mall then your neutral and ground will be bonded in the transformer .
I've been wrong before but I'm sure this is the case..:lol:
250.24 Grounding Service-Supplied Alternating-Current Systems.
(A) System Grounding Connections. A premises wiring system supplied by a grounded ac service shall have a grounding electrode conductor connected to the grounded service conductor, at each service, in accordance with 250.24(A)(1) through (A)(5).
(1) General. The grounding electrode conductor connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.
Informational Note: See definitions of Service Drop and Service Lateral in Article 100.