On a sub feed panel to a out building 4 wire 120/240 single phase do you connect the GEC to the neutral bar or the grounding bar.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The ground bar, the neutral is isolated from the metallic parts of the system in a sub-panel in a separate structure.
 