DOCTOR OFFICE WIRING

Status
Not open for further replies.

LEO2854

Esteemed Member
Location
Ma
What code section covers doctors office wiring.


ARTICLE 517 Health Care Facilities
Informational Note:  Text that is followed by a reference in brackets has been extracted from NFPA 99-2005, Standard for Health Care Facilities, and NFPA 101-2009, Life Safety Code. Only editorial changes were made to the extracted text to make it consistent with this Code.
I. General
517.1 Scope. The provisions of this article shall apply to electrical construction and installation criteria in health care facilities that provide services to human beings.
The requirements in Parts II and III not only apply to single-function buildings but are also intended to be individually applied to their respective forms of occupancy within a multifunction building (e.g., a doctor?s examining room located within a limited care facility would be required to meet the provisions of 517.10).
Informational Note:  For information concerning performance, maintenance, and testing criteria, refer to the appropriate health care facilities documents.
 
Status
Not open for further replies.
Top