Also. This was the way the electrical riser was laid out. It's 4 parallels of 500 from the transformer taping to the feed for the 3 above panels. The 3 above panels then load back into the trough feeding straight through into the building where the sub panels are.

There are a couple of potential issues here that would concern me more than the wireway.
Are these "service" conductors from a utility transformer, or are they secondary conductors from an SDS ?
 
There are a couple of potential issues here that would concern me more than the wireway.
Are these "service" conductors from a utility transformer, or are they secondary conductors from an SDS ?

The utility transformer sends 4 parallel runs of 4 #500 copper to the trough. They splice in the trough to the feeders to the above panels. Three parallel runs of 400 to one. One run of 350 to another. One run or 250 to another. All three panels then load back into the trough and feed straight through into the building. The chiller also feeds through this trough with one run of 3 300's and a 4 ground.
 

masterinbama

Senior Member
Then you would have service conductors and feeders in the same enclosure, which is a NEC violation. (someone will give you a reference number I am sure)

Can you not mount your wireway above the panels and feed the loads out of the bottom of them?
 
Then you would have service conductors and feeders in the same enclosure, which is a NEC violation. (someone will give you a reference number I am sure)

Can you not mount your wireway above the panels and feed the loads out of the bottom of them?

I Already mounted all this stuff in the same trough. I did it according to the prints. Every thing is fed underground. I would have to start all over. Which would be a disaster. Is it that the load wires off the breakers can't be in there with the wires from the transformer?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I'm away from my Code, but service conductors can not share the same raceway as non service conductors
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I'm away from my Code, but service conductors can not share the same raceway as non service conductors

You're looking for Art. 230.7. Not only is this a violation of 230.7, most all POCO's also spell this out as forbidden in their terms of service. That said, I've seen it too many times and it is just a bad practice and I don't think an AHJ or POCO should give any leeway on this.
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Not to beat up on your job, but with the MLO panels, how are you addressing the 6 service disconnect rule ?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Sorry, I am a bit confused.... do the 4 sets of 500 have any overcurrent protection ahead of your wireway ?
Also, a related question, in th event they are "feeder" taps and not service taps, how long are the
400,350 and 250 taps ?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Sorry, I am a bit confused.... do the 4 sets of 500 have any overcurrent protection ahead of your wireway ?
Also, a related question, in th event they are "feeder" taps and not service taps, how long are the
400,350 and 250 taps ?

When the OP stated that the supply conductors ran straight from "the transformer" I assumed SDS, but you are correct that we do not know.
If SDS, the secondary may be protected by the primary OCPD.
 
junior

junior

Your cable from the xfmr capacity is 1520 amps. You have three MLO DP's above the trough. I think you have three feeder CB's in each DP?=9 CB's total? To start with, this looks like a tap rule problem. My quick answer is to take out the trough and install a 1600 amp Distribution Panel with a 1600 amp MCB or Fu/Sw. with room for the 9 feeder bkrs. and space for future loads.
 