Hello, happy to be here. I am a bit new to electrical study and been awhile since study.
I need to calculate the gauge wire for a a 120V 1 phase, 1.5kW device.
Details:
12.5 amps load
Ambient temp here is 104
insulation: RHW
copper wire
I am using table 310.15(B)(16)
I decide 14AWG rated for 20amps will work. After ambient correction 310.15(B)(2) my rated current becomes 17.6amps (.88 x 20).
Now I use 240.4(D) to determine if my circuit breaker limitation, correct?
I see that for 14AWG, I can use a 15amp circuit breaker to protect 14AWG rated at 17.6 amps.
Questions:
1. Did I perform the above corrections correct?
2. Did I use 240.4(D) correct?
3. What if I only have a 20amp circuit breaker, do I have use 12AWG? But if I use 12AWG, this will not protect my 17.6amps wire because 12AWG requires circuit breaker of 20amps.
I am bit confused and want to make sure I am on the right track.
I need to calculate the gauge wire for a a 120V 1 phase, 1.5kW device.
Details:
12.5 amps load
Ambient temp here is 104
insulation: RHW
copper wire
I am using table 310.15(B)(16)
I decide 14AWG rated for 20amps will work. After ambient correction 310.15(B)(2) my rated current becomes 17.6amps (.88 x 20).
Now I use 240.4(D) to determine if my circuit breaker limitation, correct?
I see that for 14AWG, I can use a 15amp circuit breaker to protect 14AWG rated at 17.6 amps.
Questions:
1. Did I perform the above corrections correct?
2. Did I use 240.4(D) correct?
3. What if I only have a 20amp circuit breaker, do I have use 12AWG? But if I use 12AWG, this will not protect my 17.6amps wire because 12AWG requires circuit breaker of 20amps.
I am bit confused and want to make sure I am on the right track.