Hi,
An approved plan calls ,
#1 cu thhn wires feeding inside tenant sub panels of six unit apartm. Building. longest feed is 90 feed and largest demand is 70 amp and main tenant brker is 100A.

Should not be # 4 cu??
 

buzzbar

Senior Member
Location
Olympia, WA
Occupation
Electrical Contractor
The wire does seem oversized quite a bit. It could be #4 if the system is 120/240 single phase, but would have to be #3 if a three phase system (I am guessing it is the former). Any derating for any reason?

What difference does it make whether it's a three phase or single phase system? Amps is amps, right? Please explain that.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What difference does it make whether it's a three phase or single phase system? Amps is amps, right? Please explain that.

I would guess that he's saying a 120/240 volt system would allow the use of Table 310.15(B)(7).
 