james_mcquade
Senior Member
Hi all,
i was at a site last week in which the wiring in the conduit melted.
asking questions as one would i told them that you had to derate the ampacity of the wire due to the 14 conductors (#4).
derate due to the heat and that they also had to use the 70 deg c wire rating due to the lugs and breaker rating.
they didn't like my answer. they put the thhn wire back in and let it go, then the wire melted again.
turns out that they removed several feet of earth that covered a pipe to allow for molten slag to flow better.
the air temp comming out of the pipe was 200 degrees.
#1 did i miss state something?
even thhn wire cannot withstand temperatures in the 300 plus range and i told them that. they said thats what the conduit was for, to protect the wire.
also, i also read on another post that the 90 deg column was for wire derating only.
i thought that if you had 90 deg breaker, lugs and wire you could use that column to do your derating,
but if your lugs, breaker, or wire was rated 70 deg, then use that column?
Would someone please clearify these items.
thanks,
james
i was at a site last week in which the wiring in the conduit melted.
asking questions as one would i told them that you had to derate the ampacity of the wire due to the 14 conductors (#4).
derate due to the heat and that they also had to use the 70 deg c wire rating due to the lugs and breaker rating.
they didn't like my answer. they put the thhn wire back in and let it go, then the wire melted again.
turns out that they removed several feet of earth that covered a pipe to allow for molten slag to flow better.
the air temp comming out of the pipe was 200 degrees.
#1 did i miss state something?
even thhn wire cannot withstand temperatures in the 300 plus range and i told them that. they said thats what the conduit was for, to protect the wire.
also, i also read on another post that the 90 deg column was for wire derating only.
i thought that if you had 90 deg breaker, lugs and wire you could use that column to do your derating,
but if your lugs, breaker, or wire was rated 70 deg, then use that column?
Would someone please clearify these items.
thanks,
james