As the title says, what kind of shock risk is there with 14 V DC and 0.6 A when coming from a DC Power Supply?
Last edited:
As the title says, what kind of shock risk is there with 14 V DC and 0.6 A when coming from a DC Power Supply?
:blink: I hope they paid those test subjects REALLY well.For general interest:
First graph is of sticking electrodes on a subjects tongue, above 10 mA it is painful to most folks.
9V battery is bearable as a battery test though, do it all the time - just a tingle means the battery is dead, very unpleasant jolt mean a good battery. Very slight sour taste sensation from just a 1.5 V battery, 6V lantern battery you know it is a shock.
2nd graph is the change in foot to foot resistance when both feet in separate buckets of saturated salt solutions to above ankle, one foot one terminal, other foot to other terminal - DC slightly higher resistance than ac
You can use this 3rd slide to extrapolate to dc, note that above 20 mA 1/10 of 1% of the population (according to Chuck Dahziel's experiments) will go into ventricular fibrilation, fatal if not corrected (e.g. defibrillator)
Again, this is for the feet in saturated salt solution, at 60 Hz.
As you can see, a very small percentage of the population 'could' die with 14 V under these conditions. The lowest recorded electrocution fatality was at 18 Vac, according to an old paper from Indemnity Ins. company of SF.