hi
I have 3 phase motor with FLA=30A and the site temp is 50c and I need to use 6 conductors instead of three conductors
and I need to check f the below selection is correct:-
so , is this mean that I need to use 1.25 for continuous load with temp derating and no of conductor carrying derating???(3 factors at the same time)???
thank alot.
| LOAD | FLA | CALCULATION | TEMP DERATING | no of conductor carrying ampacity | Selected Wire Size AWG |
| motor 1 | 30A | 1.25x30=37.5A | 0 | 0 | 8 AWG |
| (30X1.25)/0.75=50A | 0.75 @50C | 0 | 8 AWG | ||
| (30X1.25)/0.75/0.8=62.5A | 0.75 @50C | 0.8 @ 4-6 WIRES | 6 AWG |
thank alot.