Searching for code section about low & high voltage cables together in a raceway. Haven't had the issue in a long time, was asked about it last night. Near as I recall, a 120 volt cable cannot go in a raceway with LV or data cables, especially if not for the same equipment.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
See 300.3(C). Pay attention to the IN's

Roger
 

jmellc

Senior Member
Location
Durham, NC
Occupation
Facility Maintenance Tech. Licensed Electrician
I found a better way to do this.

I ran 1 LV cable to new location for a LV timer switch.

I ran a 2nd LV cable to new location for a 277V 3 way switch. I mounted a RIB relay at the old location & fed it with cable, using common, NC and NO leads on the 3 way leads. Put SP switch at new location. Put 24 volt power supply at new location & fed switch with it. Works like a charm.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
I suppose your installation is compliant if there is a divider between the voltages in the box.
Many things work although not compliant.
 