yesterlectric
Senior Member
- Location
- PA
- Occupation
- Electrician
I am doing a tie in for a solar installation and the general contractor wants us to tie in on the line side of the 4000 amp disconnect and put a building load meter with voltage monitoring on the line side of the disconnect as well. I have not verified the total possible short circuit current deliverable by the transformers, but the current 480 volt switchgear is rated at 150K amps. I am needing to install a circuit breaker between the voltage input taps and the meter. i am finding it difficult to find a 5 amp breaker with an interrupting rating greater than 14K amp. The "engineer" on this project seems less knowledgeable than myself. What is usually done in this circumstance? Are specialty fuses required? Is this typically not a concern?