Service vs Feeders

Status
Not open for further replies.

Bōssie

Member
Location
Tioga, ND
I come from the pole to the transformer, from the transformer to a disconnect. My neutral stops at the disconnect and I feed a 3 phase 480 Volt Panel 200 feet away. Is the cable from the disconnect to the Panel considered "Service Conductors" or "Feeders"?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Service conductors stop at the service (first) disconnecting means. Beyond that point wiring is feeders or branch circuits.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The original post did not advise if it was a POCO or cutomer transformer plus there may be pole disconnects.
 